We all know that if you want to change the rotation of a three  phase AC motor.) i2 u4 j8 h0 [* U  p! L& i. ~
Just swap any of the two phase leads.4 g* w5 [6 D0 z: l8 S- ^/ |0 _
But for VFD application you need to do the swap after the inverter.8 }! z* g3 Q! L" o5 ^0 z
If you swap the leads before the inverter, it will not work.
鲜花(0) 鸡蛋(0)
发表于 2010-4-14 18:18 | 显示全部楼层
go go go
鲜花(0) 鸡蛋(0)
发表于 2010-4-19 14:38 | 显示全部楼层
Yes, Good point.; [+ j4 o8 j- W9 x
" d( c3 ?& K# }5 k
As the principal of the VFD works, bascially from AC to DC, then DC to AC.
' J( O* _3 ^. X3 c5 j0 X* L( M
2 D1 b! k; d7 u' o4 e( u, y5 nThe phase rotation of the output of the VFD connecting to the motor is based on the sequence "open" or "close" controlled by the inverter pre-set inside; any changes to the phase rotation of the feeder will not affect the DC rotation, as DC is NO phase at all.
5 I( }6 [" l# t6 y: M
5 v( E# _9 ?: W+ s/ u& N  F) JThe only thing you can change the rotation of the motor is the output side of the VFD, NOT the input of the VFD.