We all know that if you want to change the rotation of a three  phase AC motor.7 C( p5 B; x) s1 Y  n# \8 [
Just swap any of the two phase leads.$ b- Q$ \) z% ?) Y1 ?2 h- }) g
But for VFD application you need to do the swap after the inverter.
- @1 t+ s" K) p, ^( v- KIf you swap the leads before the inverter, it will not work.
鲜花(0) 鸡蛋(0)
发表于 2010-4-14 18:18 | 显示全部楼层
go go go
鲜花(0) 鸡蛋(0)
发表于 2010-4-19 14:38 | 显示全部楼层
Yes, Good point.
8 r# C- d5 r4 v3 X7 z2 i/ g2 S0 P. d
7 X4 n: a# h* mAs the principal of the VFD works, bascially from AC to DC, then DC to AC. ) Z, z3 ~1 k' I- g/ M6 n( C# C% X

+ X7 O9 L5 Q3 e/ f/ q& lThe phase rotation of the output of the VFD connecting to the motor is based on the sequence "open" or "close" controlled by the inverter pre-set inside; any changes to the phase rotation of the feeder will not affect the DC rotation, as DC is NO phase at all.& X+ c, @! S+ d; I. m. i  Z8 q
7 L  u6 w* }, b2 v8 _1 S$ @
The only thing you can change the rotation of the motor is the output side of the VFD, NOT the input of the VFD.